Softus said:
Is there a law against cutting it?
If so, what is that law?
Is there a law against removing the DNO fuse in order to work safely on an installation?
If so, what is that law?
Yep. The Electricity Safety, quality and Continuity Regulations 2002, Statutory Instrument No. 2665.
Clause 25 (1) No person shall make or alter a connection from a distributor's network to a consumer's installation, ... without that distributor's consent, unless such consent has been unreasonably withheld.
The DNO is constrained by clause 24 of the same regulations:
24. - (1) A distributor or meter operator shall ensure that each item of his equipment which is on a consumer's premises but which is not under the control of the consumer (whether forming part of the consumer's installation or not) is -
(a) suitable for its purpose;
(b) installed and, so far as is reasonably practicable, maintained so as to prevent danger; and
(c) protected by a suitable fusible cut-out or circuit breaker which is situated as close as is reasonably practicable to the supply terminals.
(2) Every circuit breaker or cut-out fuse forming part of the fusible cut-out mentioned in paragraph (1)(c) shall be enclosed in a locked or sealed container as appropriate.
So if someone removes the seal, the DNO's not complying with the law. So it won't allow you to remove the seal.
If you go ahead anyway, you are trespassing on the DNO's property. Now I can't quote a law on trespass because it's common law. You can't be prosecuted for trespass (in spite of notices such as 'trespassers will be prosecuted').
Now I don't
know what happens if you break the seal. I can only guess, but I'm not about to do so.