Introduction to the draft for public comment (DPC) of 17th IEE Regs said:The following major changes are incorporated in Part 7:
Section 701 Locations containing a bath tub or shower basin.
Zone 3 is no longer defined.
Each circuit in the special location must have 30 mA RCD protection.
Supplementary bonding is no longer required providing the installation has main bonding in accordance with
Chapter 41.
streetlighter said:Nothing worse in my view than an electric shower on a BS3036 with no RCD protection usually 6mm cable and they have installed a 9.5kw to replace the old one.
Then you get the "its worked fine for years" response when you tell the owner the wiring needs to be upgraded.
scousespark said:What exactly are you planning on doing to fix this?
mdbalson said:scousespark said:What exactly are you planning on doing to fix this?
I am going to replace the Consumer unit with a split-load one.
Disconnect the double socket & put it into the ring circuit.
Change the ccu for a 45mm 1gang surface box, put a 40 amp terminal block inside the surface box, & put a 1 gang blank plate over the box.
So then the old cooker circuit is just for the shower.
mdbalson said:It is in a Bathroom in my Neighbour's house. As I am putting right some boges done by a "Well praised Qulifyed Industrial Electrician"(At other jobs that he had done).
I will make a New post later on, after I have done the jobs, and there maybe some pictures of the boges & of the remedial work, which I will post up.
scousespark said:Why are you changing the CU, but still using the rubbish design you've come across. The correct way would be to run a new circuit straight to the shower.
What state is the current installation in, given you've decided to do a CU change?