Double socket earth connection

Here is a scenario to consider. One of the live wires chafes (ie no grommet used) and makes contact with the metal back box or plate screw (I have often seen faceplate screws that have gone through conductors because the wires weren't pushed neatly into the back box).

You have a plastic socket but the now live back box conducts through the two screws so you have two live metal screws on the plastic faceplate of your socket waiting to bite the unwary. This is the reason you should put another wire from the plate to the back box if it's metal. It doesn't matter what others have done in the past, two wrongs don't make a right as Mum used to say.

Can't tell from your photo if it's a metal back box or not. Which is why you should look at the box when doing this job.
I do not recall seeing a plastic socket that does not have the earth bar extending to brass surrounds around the screw holes, therefore providing the faceplates earthed, and the screws tight, the aboves unlikely
Saying that i opt to earth the backbox regardless ,often returning to the van to get a stupid bit of cable to do so
 
As a decorator, I would rather that all metal back boxes were earthed. I have lost count of the times that a live popped out as I loosened the socket faceplate so that I could paper behind it.

Yes, wires pop out. Why would separately earthing the back box help?

Frankly, I consider the lack of an earth to the metal back box as a sign of laziness.

Personally I put it somewhere on the spectrum of thing “often seen but not necessary”, to the left of earth wires connected to taps fed by plastic pipes but to the right of upgrading a CU to include RCDs.
 
both terminals are linked on the back of the faceplate anyway mate, it's just dual earth for high integrity circuits. you can pop one bare earth wire (sleeved in green/yellow obviously) into each terminal or shove both together into the same one if they fit cleanly, makes zero difference on a standard ring. just make sure you still run a little fly lead from one of the earth terminals into the metal back box lug so the casing is properly bonded.
 
Only where those sockets can never be used by persons of capability BA1, which is almost nowhere.
Almost, to quote Joe Lycett, doth butter no parsnips.

There are a few situations where an RCD can be omitted, which is what the RA is for.
 
I do not recall seeing a plastic socket that does not have the earth bar extending to brass surrounds around the screw holes,
They have existed, such as this 'HLM' branded effort.

hlm_socket.jpg
 
I don't have a copy of 1363; they are so prohibitively expensive.

I have bought BS1363 accessories with only one fixing hole having a connection to earth.
 
I don't have a copy of 1363
I think there is a lot of room for differing opinions.

10 Provision for earthing
10.1 Socket-outlets shall be so constructed that, when inserting the plug, the earth connection is made
before the current-carrying pins of the plug become live. When withdrawing the plug, the current-carrying
parts shall separate before the earth contact is broken.
10.1.1 Compliance shall be checked by inspection and electrical test.
10.2
All accessible metal parts of socket-outlets shall be in effective electrical contact with the earthing
socket contact, except that metal parts on, or screws in or through, non-conducting material, and separated
by such material from current-carrying parts in such a way that in normal use they cannot become live,
need not be in effective electrical contact with the earthing socket contact.

NOTE Metal parts having an accessible surface coating of lacquer or enamel are accessible metal parts within the meaning of this
requirement.

10.2.1 Compliance shall be checked by inspection and the following:
a) for metal parts insulated from live parts, by the test described in 15.1.3;
b) for metal parts connected to an earthing terminal by the following test. A current of 25 A ± 0.75 A,
derived from an a.c. source having a no-load voltage not exceeding 12 V, is passed for s between the
earthing terminal and any accessible metal part intended to be earthed and between the earthing
terminal and an earthing plug pin inserted in the earthing socket contact;
c) the resistance between the earthing terminal and any other nominated part shall not exceed 0.05 7.
10.3
If means are provided for electrically bonding the mounting box to the earthing circuit of the
socket-outlet by means of the fixing screws the connection between the screw and earthing terminal shall
be of low resistance.

10.3.1 Compliance shall be checked by the test described in 10.2.1b) applied between the socket-outlet
earthing terminals and any fixing screw in electrical contact with the earthing circuit. For the purpose of
this test the socket-outlet shall be attached to its appropriate mounting box, the fixing screws being
tightened to a value of two-thirds those given in Table 3a.

[Quoted under fair dealing law in Section 30(1ZA) of the Copyright, Designs and Patents Act 1988 (added in 2014).]
 