I have a problem with a downlight in my kitchen in as much as a 2.5mm cable and a 1.5mm cable are going into a junction box is this what is causing it to blow.thanks
 
A change in conductor size won't cause a fuse/MCB, RCD or lamp to blow unless it is overloaded to the point where the insulation is knackered

If you give us some more info we might be able to offer some useful advice. What is actually 'blowing'? What size fuse/MCB is protecting the circuit. Where does the feed for the junction box come from? Do any of the cables run through adverse conditions (damp, insulation, rodents, etc etc)? What lamps are fitted in the downlights?
 
1. Why do you have 1.5 and 2.5 connected together? IMO this should never happen without a fuse in between.

2. What have you done recently to cause the fuse to blow?
 
Crafty said:
1. Why do you have 1.5 and 2.5 connected together? IMO this should never happen without a fuse in between.

What if the protective device was 6 or 10amps? You would still insist on a fuse between the change of conductor sizes?
 
Crafty said:
1. Why do you have 1.5 and 2.5 connected together? IMO this should never happen without a fuse in between.

?

more to the point why has he got two cables between the JB and the light ?
 
GaryMo said:
Crafty said:
1. Why do you have 1.5 and 2.5 connected together? IMO this should never happen without a fuse in between.

What if the protective device was 6 or 10amps? You would still insist on a fuse between the change of conductor sizes?
No, however why have two conductor sizes on the same circuit? (except insulation, derating etc)
 
Crafty said:
GaryMo said:
Crafty said:
1. Why do you have 1.5 and 2.5 connected together? IMO this should never happen without a fuse in between.

What if the protective device was 6 or 10amps? You would still insist on a fuse between the change of conductor sizes?
No, however why have two conductor sizes on the same circuit? (except insulation, derating etc)

Is there a regulation stating that differing sizes of conductors can't be used on the same circuit providing that the smallest conductor can carry current which is equal to or larger than the design current and size of protective device (factors taken into consideration)?

I agree it's not best practice though.
 