earth electrodde
Yep, always do the MEB's in 10milli.
I would also always look to provide PME if it would be available - the cost of this verse a rod and 100mA RCD is actually cheaper.
plugwash said:
Spark123 said:
2.5mm² protected against corrosion and mechanical damage (seems rather small though imo)
I'd think 2.5mm should take 240A for long enough to take out a RCD, especially given that it should be starting from cold
anyone fancy calculating the adibatic for the trip time of a type S rcd, a starting temp of room temperature, the limiting temp of PVC insulation and an EFLI of 1 ohm?
Taking K to be 143 (70 degree PVC, starting from cold)
K²S² = 143² x 2.5²
= 20449 x 6.25
= 127806.25
240volts over 1 ohm = 240 Amps
I²t must be a max of 127806.25
t must not exceed 127806.25/(240²)
=127806.25/57600
= ~ 2.2 seconds which is AFAIK, far greater than the trip type on an S type RCD
[/i]