D
Deleted member 310928
Which can sometimes be beneficial if the manufacturer may not feel confident that the item will remain as a class 2.Most other light fittings have earth terminals, even if they are Class II.
Which can sometimes be beneficial if the manufacturer may not feel confident that the item will remain as a class 2.Most other light fittings have earth terminals, even if they are Class II.
I suppose it depends upon what you mean by a 'light fitting', but I'm not at all sure about that. For example, as you go on to acknowledge, an increasing number of 'throwaway' LED lights appear to have no terminals all, just a bit of 2-core flex dangling out of them so ....Most other light fittings have earth terminals, even if they are Class II.
"A space to tuck in a connector for the spare CPC" presumably would not have qualified as the terminal required by 14th edition and, although, as you say, the lead dangling out of others will go to a junction box, where a terminal can be provided for the CPC, I would have thought that the light ('fitting') itself would have qualified as a 'lighting point' which would have required an 'earth terminal' under 14th, wouldn't it?Anything that doesn't should have space to tuck in a connector for the spare cpc, or else the fitting will have a lead attached which will go to a junction box and the cpcs will terminate in there.
Only if the 'earth terminal' is actually connected to something - rather than just being a 'floating parking space' as it often is.Which can sometimes be beneficial if the manufacturer may not feel confident that the item will remain as a class 2.

Purely for continuity purposes, isolated from the fitting.Are you sure about the Class II ones.
Surely having a CPC in a Class II item is not desirable.
As the regulation states, it is purely in case it is needed in the future.Purely for continuity purposes, isolated from the fitting
Ok...As 412.2.3.2 states. Run to and terminated at each point in wiring and at each accessory.
... but Class II fittings will not have an earth terminal.Well, all ceiling roses, boxes, pattresses, junction boxes etc have earth terminals. Most other light fittings have earth terminals, even if they are Class II.

I didn't realise we were suddenly comparing modern fittings with a 60 year old book of regulations.I suppose it depends upon what you mean by a 'light fitting', but I'm not at all sure about that. For example, as you go on to acknowledge, an increasing number of 'throwaway' LED lights appear to have no terminals all, just a bit of 2-core flex dangling out of them so ....
"A space to tuck in a connector for the spare CPC" presumably would not have qualified as the terminal required by 14th edition and, although, as you say, the lead dangling out of others will go to a junction box, where a terminal can be provided for the CPC, I would have thought that the light ('fitting') itself would have qualified as a 'lighting point' which would have required an 'earth terminal' under 14th, wouldn't it?
As above. 412.2.3.2.Today, there is a requirement to run a CPC to every point/accessory, but no requirement of which I'm aware to 'connect' it to anything - and nor do many present day 'lighting points' have an 'earthing terminal', do they?
Well, you wrote of light fittings, ceiling roses, boxes, pattresses, junction boxes etc. and "anything which didn't have an earth terminal" in the present tense, and also mentioned "Class II" (did that concept {or 'ceiling roses'} exist 60 years ago?) so, yes, I thought you were essentially thinking of 'modern fittings'.I didn't realise we were suddenly comparing modern fittings with a 60 year old book of regulations.
Yes, but as I said, 412.2.3.2 requires the CPC to be 'terminated' at every point and accessory in a circuit, but that does not (and, in many cases, cannot) necessarily mean that the CPC is 'connected to' anything other than the terminal, does it?You said: .... As above. 412.2.3.2.

Maybe. But a reg we should keep to.As the regulation states, it is purely in case it is needed in the future.
A daft reason for a regulation in my opinion.
What? Like the Aurora AU150? Double Insulated with earth terminal to provide continuity......... but Class II fittings will not have an earth terminal.
What does "earth terminal to provide continuity" mean? Continuity between what and what?What? Like the Aurora AU150? Double Insulated with earth terminal to provide continuity......

Of course Class II, double insulation and ceiling roses existed 60 years ago.Well, you wrote of light fittings, ceiling roses, boxes, pattresses, junction boxes etc. and "anything which didn't have an earth terminal" in the present tense, and also mentioned "Class II" (did that concept {or 'ceiling roses'} exist 60 years ago?) so, yes, I thought you were essentially thinking of 'modern fittings'.
I'm not quite sure what you are trying to say here.Yes, but as I said, 412.2.3.2 requires the CPC to be 'terminated' at every point and accessory in a circuit, but that does not (and, in many cases, cannot) necessarily mean that the CPC is 'connected to' anything other than the terminal, does it?
If it has any metalwork...In a Class I luminaire, the terminal will be connected to the metalwork. In double...
Thanks - but as for "of course", I obviously did not know (at least about the 'Class II') which is why I asked the questionOf course Class II, double insulation and ceiling roses existed 60 years ago. Both are older.
If there is any. Many/most of the Class II items I have do not have any metalwork (at least, not 'touchable metalwork') to which on could connect anything!I'm not quite sure what you are trying to say here. .... In a Class I luminaire, the terminal will be connected to the metalwork...
I suppose I've just been questioning the meaning of your choice of words. You again write "for continuity purposes" which leads me to again ask "continuity between what" and what? I presume the underlying concept you're trying to get across is that the CPC is there "in case needed in the future" but I would be more certain of that if you had written something like that, rather than repeatedly talking about 'continuity'. In double insulated fittings or accessories, the terminal will just be there for continuity purposes and not connected to anything.
The classic situation is a lighting circuit with loop and CPC terminal at the rose providing continuity to the switch and of course subsequent roses and switches...I suppose I've just been questioning the meaning of your choice of words. You again write "for continuity purposes" which leads me to again ask "continuity between what" and what? I presume the underlying concept you're trying to get across is that the CPC is there "in case needed in the future" but I would be more certain of that if you had written something like that, rather than repeatedly talking about 'continuity'![]()

Read what I put. I was talking there about Class I luminaires.If there is any. Many/most of the Class II items I have do not have any metalwork (at least, not 'touchable metalwork') to which on could connect anything!
This is all hinging around the regulation that EFLI first quoted.I suppose I've just been questioning the meaning of your choice of words. You again write "for continuity purposes" which leads me to again ask "continuity between what" and what? I presume the underlying concept you're trying to get across is that the CPC is there "in case needed in the future" but I would be more certain of that if you had written something like that, rather than repeatedly talking about 'continuity'![]()
Ah, I see. That is why we have been writing somewhat 'at cross-purposes'!The classic situation is a lighting circuit with loop and CPC terminal at the rose providing continuity to the switch and of course subsequent roses and switches
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local