Oh, in that case, I guess I was not talking nonsnese last nightEasiest to put it this way, All the connections to earth I am talking about are the sole connection for the transformer.
Kind Regards, John.

Oh, in that case, I guess I was not talking nonsnese last nightEasiest to put it this way, All the connections to earth I am talking about are the sole connection for the transformer.
with no earthing of the neutral at the transformer, I can't see that the supply could possible be called TN-C-S!
Well, per than definition you give (the question at the start of the above quote), everything you go on to say is true.Finally - Is the fault-current path caused by an earth fault on the installation separate from the neutral or combined with it? Within the installation it's separate, but due to the E-N bond at the service entrance, it's then combined with the distribution neutral from the supply transformer. So there's the C-S. So it's not P.M.E. because there's only one earthing point, but it's still TN-C-S by the latter's definition.
Indeed. PME clearly needs an 'M'!We'll probably end up in a hamster wheel! What is agreed is it not PME.
I'm not sure that resolves the question, does it? My understanding has hitherto been that for it to be -C (i.e. TN-C-S) there has to be at least some length of a single conductor, after the joining of the neutral and earth at the DNO end, which represents both a return to neutral and a potential path to earth when viewed from the consumer's end. Is that right or wrong?We'll The section of neutral from the transformer to the point at which it earthed is the same for any type of DNO or private system I have ever seen be it TNS or TNCS. If it were in a DNO fuse board and the cables leaving it were PILCs it would generally be TNS.
I suppose that 'functional' definition probably makes more sense than the more 'structural' one I've been brought up on - and I see that Part 2 of the regs defines TN-C-S in terms of 'combining neutral and protective functions' in one conductor. Of course (and this is probably why I haven't had to have this discussion before) both of the definitions will usually give the same answer for straightforward conventional TN-S and TN-C-S systems; it's only with this 'PNB' system that the two approaches seem to give different answers.I'd always taken it that the C/S part of TN-S or TN-C-S refers to the overall path of the fault current between the installation and the supply transformer.
Where isolated premises are connected to a local transformer which provides connection to no other customers, for example, it is possible to use Protective Neutral Bonding (PNB). PNB is not PME, and is not subject to the PME provisions of the ESQCR excepting that Regulation 8(3)(b) makes specific provision for this method of earthing.
In this method of earthing, the LV neutral is not earthed at the transformer, but instead is earthed at the cut-out. No bonding is required. In this way a broken neutral anywhere on the system does not result in elevated potentials on metalwork.
PNB is the preferred method of earthing in these cases, and is particularly effective where livestock is involved. All PNB installations shall be recorded on the mains records.
The resistance to earth of the earth electrode shall be such that twice the current necessary to operate the HV protection will flow following an inter-winding fault on the transformer.
A value of 40Ω or less shall be achieved.
That's somewhat wishful thinking isn't it, given the likely Ze? ... but I guess it depends upon what the 'elevated' is relative to!.... but instead is earthed at the cut-out. No bonding is required. In this way a broken neutral anywhere on the system does not result in elevated potentials on metalwork.
That's somewhat wishful thinking isn't it
Probably because its fed by a privately owned transformer