Earthing the armour

Joined
24 May 2007
Messages
218
Reaction score
0
Location
Surrey
Country
United Kingdom
If the armour is not being used for earthing function does it still need any connection at all ie. earthed at one end?
 
No, one end, unless a single core SWA - which would never be installed in a domestic, and would have to be an aluminium armour!
 
You can earth at both ends if you like, but you MUST earth at least one end. (Best practice to earth it at the supply end if only doing one end)

The whole point of installing SWA (or concentric or split concentric for that matter) is so that if the cable is penetrated by something such as a spade, nail or anything else metal then it will contact the armour first before it hits the live wire.

This will automatically cause a dead short and will operate the OCPD or RCD supplying that circuit, removing the chance of electrocution.

If the armour is not earthed then any penetration which makes contact with the live wire will bring all the armouring live, and also the metal object which has penetrated the cable.

If this is a spade for example then this is not good and could well kill the spade weilder. :shock:
 
What is the best way to achieve this? The SWA will be supplied via a 60A insulated isolator.
 
Use a metal isolator, or terminate the SWA into an earthed metal enclosure such as an adaptable box, or as a last resort, if the plastic enclosure is strong enough to terminate the gland directly into then you can earth the gland using the banjo supplied in the gland pack.

How big is the SWA? Could you use split concentric cable instead?
 
Too late, already bought the SWA, but you are spot on it would have been easier.

Can you direct me to the type of adaptable box I can use.

Cheers
 
Just a standard adaptable box, probably 100mm x 100mm x 50mm.

Gland the SWA into the bottom of the adaptable box, and pass the cores straight into the switch fuse (I hope you meant to write switch fuse, not just an isolator). Then take a 10.0mm² earth from the earth terminal in the switch fuse, and bolt it to the hole in the SWA gland banjo.
 
RF Lighting said:
The whole point of installing......split concentric........is so that if the cable is penetrated........it will contact the armour first before it hits the live wire.

Not quite true for split...It may hit the neutral then the live?
 