I take it you don't have many dealings with YEDL
Spark123 said:Are you aware of the diffenences between TN-S and TN-CS and the requirements?
an RCD works by tripping when there is current going to earth so if the neutral doubles as the earth there will always be some current going to neutral/earth so will continually trip the RCD.
securespark said:Did you disconnect MEB's when testing Ze?
If not, then do so & retest. It may be that you have nothing off that earth on the conduit and your earth connection is actually via the service pipework. This has never been allowed (in the case of gas pipes) and not been allowed since 1966 (in the case of water pipes).
bryan walker said:I hope they will be able to convert to TNS.