Sorry copied and pasted from your post. I assumed it must have been in amendment 1 which I never bought.Eric, if you are literally looking for 735.411.3.2, that does not exist, and never has existed; indeed there is no Section 735.735.411.3.2 was not in BS7671:2008 (At least I can't find it.) only in BS7671:2008 Amendment 1 so that document they have sent you is out of date.
What you should be looking for is 753.411.3.2, which was present in the original BS7671:2008 in exactly the same form as in the 2011 Amendment.
Kind Regards, John
I also had problems with underfloor heating fitted by a builder where he had caught the cable and repaired with insulation tape. I had to rip up all tiles and replace the whole lot. It took phone calls also to find out if suitable for under a wet room and after all that useless anyway.