Spark123 said:
A switch disconnector isn't an overcurrent protective device.
Just to expand a little for the OP
A BS5419 device is a switch disconnector. It is not an MCB, therefore it does not have a max permitted Zs, as regardless of how large or small a fault were to occur the BS5419 device will not trip (because they are just a switch).
On the MEW cert. you need to put the characteristics of the OCPD which feeds the switch disconnector you have replaced.
As a side note, I thought BS5419 had been superseded by BSEN60947-3
Does anyone know if they still make BS5419 isolators?