    There's probably not a single answer to this but in the hope for a bit of enlightenment, is there anything in particular which causes the entire board to trip rather than just the circuit breaker/fuse itself?

    It's been happening for a 2-3 months now. The board is 1 of 3 we have, and they were all rewired 5 or 6 yrs ago after a bit of house restoration. Unfortunately, our garden lights don't have their own isolation box – I immediately thought it was these causing the problem (water getting into junction boxes/outdoor switches) as it appeared to be happening when someone went outside and the lights came on. So I looked at the boxes, and yes, there was damp inside one so I fixed that and wrapped in polythene. It seemed to be Ok for a while. However, the board also tripped when other lights in the house were switched so was this just a coincidence. Sometimes the main board switch won't reset immediately, it takes a few attempts.

    There is a main junction box for our electric gate where the garden lights cable spurs off from to another box. I disconnected them at this 2nd box yesterday (1st one was hard to get to) just to try to eliminate that area. Low and behold, they tripped when the kitchen lights were switched on, so it can't be to do with the garden lights.

    Could it be a faulty board, or even if the 1st garden box was damp, could this effect switches in say the kitchen when activated?

    Any help gratefully appreciated.
     
  2. Sponsored Links
  3. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    24,740
    Thanks Received:
    2,431
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Yes, an Neutral to Earth fault on a circuit can trip the RCD ( even if the MCB for that circuit is switched off ) when another circuit has a load on it.

     
  4. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,097
    Thanks Received:
    2,065
    Location:
    Oxfordshire
    Country:
    United Kingdom
    What exactly is "tripping"? I guess its an RCD, but please clarify.

    It is very unlikely to be a "faulty board". It will be one of the devices or circuits connected to it.

    Damp/moisture in electric circuits causes all sorts of problems. There are two ways to resolve this:

    1. By isolating devices/circuits one at a time. Remember when isolating, you need to disconnect both the live and the neutral to the circuit. NOTE: Many switches (and the MCBs in your consumer unit) only turns off the live conductor. So you may need to take wires out.

    2. By getting an experienced electrician with an Isolation Resistance tester to make a structured examination of your problem.

    PS. If you have/had damp in an external circuit then it needs fixing properly. Water will get in anywhere if it can and wrapping in polythene will not mend it.
    Properly installed external electrics do not suffer from ingress of water.
     
  5. Deansplit

    Deansplit

    Joined:
    5 Oct 2005
    Messages:
    576
    Thanks Received:
    2
    Country:
    United Kingdom
    Ah, thanks, Bernard. Just to confirm we're understanding - the MCB's on the rest of the board aren't switched off, they're all on. What I meant was if the fault 'is' with the outside junction box/connection, but outside lights aren't on (but MCB for that circuit is), then when other lights are switched on, eg kitchen, this can still trip the board due to the fault with the outside box?
     
  6. Sponsored Links
  7. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    24,740
    Thanks Received:
    2,431
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Yes it can, To check the circuit one has to disconnect both Live and Neutral of the suspect circuit to prevent the Neutral - Earth fault from tripping th RCD.
     
  8. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,097
    Thanks Received:
    2,065
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Oh, how I wish I had remembered to mention that….
    :D
     
  9. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    24,740
    Thanks Received:
    2,431
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Yes I missed that bit , sorry TTC
     
  10. crystal ball

    crystal ball

    Joined:
    28 Apr 2004
    Messages:
    4,513
    Thanks Received:
    256
    Country:
    United Kingdom
    They may be properly installed at the time but future mistreatment may well allow ingress of water, as well as age deterioration
     
  11. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page