I do not disagree that, according to BS 7671, flexible or pliable conduit cannot be used used as a protective conductor [543.2.1].
The basis for this is that these containment systems can, and all to often do, fail when subjected to mechanical stress. A common mode of failure is that the conduit parts company with the gland that is supposed to secure it, and that also provides an electrical connection to the metallic parts of its sheath. This will most often be due to excessive stress.
Whilst such stresses may be possible when the conduit can be subject to movement, it is far less likely that this would happen if movement is restricted. Now this would be the situation if the conduit were to be used to contain wiring concealed within a wall or partition [522.6.6], or within a wall or partition with metallic internal parts [522.6.8].
Flexible or pliable conduit usually has a substantial metallic sheath that would be very unlikely to vaporise under the sort of fault conditions that might be encountered on a final circuit supply items such as 13A socket outlets.
So it could offer a solution to some of the situations where a sheath is required to act as a protective conductor. All it needs is for JPEL/64 to get its act together and act

. It would offer superior protection to that provided by the BS 8436 cables that I have looked at - these have fault current limitations and many people seem to be unaware of them.