I investigate reports of such a bang a few years back, after the customer told me where he thought the noise came from I looked under floorboards.
T & E hanging down under the floor and laying on damp soil. Pinhole in cable (might have been there since installation some years previous).
I deducted that dirty water had penertrated, caused a short, rapid heating of cable caused the "bang" and cleared the fault at the same time and ready to start the procedure again hours later the time period dependant upon the actual dampness of the soil at the time.
Renewed cable,clipped it up and clipped up all other nearby cables hanging in a similar fashion.
The problem never returned over ten plus years compared to between once to six times a day.
So I recckoned probably sorted.
(Rewireable 30A fuses and no RCD).