Lighting circuit.
L-N 243v
L-E 70v
N-E 57v
Connections at lights OK connections at CU OK
When I have come across this before it has been a snipped CPC at a junction box. Had a good look and can't find any junction boxes that connect this circuit..
By that I mean when the faulty circuit is live and the other lighting circuit are switch off at the MCB the junction boxes I have found have no power.
I have found these junction boxes and a few have snipped cables i.e.
It looks to me like some one has just needed the neutral.
Now since this circuit is dead when the faulty circuit is live, I have been thinking this junction box has nothing to do with the faulty circuit.
But could it be?
Impossible for you to answer I guess....
But if I come across situations such as this is it best practice to reconnect the CPC.
Also what do you think is going on in the JB
Thanks
L-N 243v
L-E 70v
N-E 57v
Connections at lights OK connections at CU OK
When I have come across this before it has been a snipped CPC at a junction box. Had a good look and can't find any junction boxes that connect this circuit..
By that I mean when the faulty circuit is live and the other lighting circuit are switch off at the MCB the junction boxes I have found have no power.
I have found these junction boxes and a few have snipped cables i.e.
It looks to me like some one has just needed the neutral.
Now since this circuit is dead when the faulty circuit is live, I have been thinking this junction box has nothing to do with the faulty circuit.
But could it be?
Impossible for you to answer I guess....
But if I come across situations such as this is it best practice to reconnect the CPC.
Also what do you think is going on in the JB
Thanks