Fiddly Kitchen Socket

I would have no problem protecting 1mil with a 13A fuse (in my own house at least).

It's better than the umpteen extension leads with 0.75 when they have 8+ outlets, and you could never begin to guess what kind of load they could be subjected to
 
, that it probably takes around 22A to blow a 13A BS1362.
Does the stated CCC not allow for that?



Therefore, consequently, does any conductor in normal use ever approach 70°C?
Therefore, consequently, can we reduce volt drop values and increase maximum Zs slightly.
 
, that it probably takes around 22A to blow a 13A BS1362.
Does the stated CCC not allow for that?
Not the CCC tables we use, as far as I can see. Those tables allow for the degree of over-current that would be allowed flow by an MCB, but not for the ~1.7In which a BS1362 will apparently allow to flow indefinitely (as compared with 1.13In for an MCB). For BS3036 fuses, the regs indicate the correction factor that needs to be applied to the tabulated CCC figures, but there is no corresponding correction factor stated for BS1362 ones.

Kind Regards, John
 