What about this:
?
Cross-sectional area.
?
Cross-sectional area.
I really don't think you should concern yourself about what are 'spurs' and what are 'branches' - as you will have seen, the terminolgy is totally confused. As I said before, the important thing for you to understand is that a single cable supplying just one socket can be 2.5mm² - even when the circuit to which it is connected is wired in 4mm² cable and has a 32A MCB.**Wow, I've missed all the excitement , I've got some reading up to do. Well, this is what I think but please correct me if I'm wrong (I'm sure I probably am anyway): ...
Cross-sectional-area (i.e.'size') of cable conductors - like 2.5mm² or 4mm².And what does CSA mean?
[** question for the electricians - given that a 2.5mm² unfused spur to one socket off a 4mm²/32A radial is permitted, that would almost seem to imply that a piece of 2.5mm² cable running straight from CU to one socket could be protected by a 32A OPD - any comments/thoughts??!]
Kind Regards, John.
As stated in appendix 15 (in the 'unfused spur' box).[** question for the electricians - given that a 2.5mm² unfused spur to one socket off a 4mm²/32A radial is permitted, that would almost seem to imply that a piece of 2.5mm² cable running straight from CU to one socket could be protected by a 32A OPD - any comments/thoughts??!]
I'm not sure that I would like to tell a lot of electricians, let alone DIYers Is this the BAS-theory that one can rely on the downstream OPD (fuses) to protect the cable - such that even a 50A MCB would be acceptable?Yes, it can - but don't tell the DIYers, it'll only confuse them or get someone hurt........20A protective device , please[** question for the electricians - given that a 2.5mm² unfused spur to one socket off a 4mm²/32A radial is permitted, that would almost seem to imply that a piece of 2.5mm² cable running straight from CU to one socket could be protected by a 32A OPD - any comments/thoughts??!]
That's really what I was asking. Is it your belief that it is technically compliant if one does remove the main circuit?I suspect (know) you knew all that so what is it, exactly, you are asking. The situation 'looks' even worse should the main circuit be removed.
I suppose it must be 'technically' compliant (because there it is)but pointless and no mention is made in appendix 15 of the restrictions.That's really what I was asking. Is it your belief that it is technically compliant if one does remove the main circuit?I suspect (know) you knew all that so what is it, exactly, you are asking. The situation 'looks' even worse should the main circuit be removed.
That's obviously the crunch - but the fact is that the situation is no different with or without the 'main circuit' connected, and most people probably interpret the regs (particularly Appendix 15, albeit only informative) as indicating that 32A MCB is always adequate to protect a 2.5mm² cable against fault current, even though whether or not that is true surely depends on the Ze/PFC?I suppose it must be 'technically' compliant (because there it is)but pointless and no mention is made in appendix 15 of the restrictions. Of course, it has to meet the fault current (and other requirements of 433) which it may not with a 50A opd. (I haven't worked it out).That's really what I was asking. Is it your belief that it is technically compliant if one does remove the main circuit?
The indicated currents are not the currents flowing but are what Tozzy believed to be the CCCs of the cables (thanks to a misleading DIYnot 'information' page).Both drawings are the same and they are both wrong - how would the current be the same after the first load, and why would a 350W load draw 20A?
Both drawings are the same and they are both wrong - how would the current be the same after the first load, and why would a 350W load draw 20A?
That is correct (in terms of current to the rads) - the only current flowing beyond the second socket would be that going to the TV (or anything else plugged into that third socket.So just to clarify I presume when you say my 2nd diagram is correct (think I got a mind blank today and thought it was wrong), i assume the current would travel like this (in red):
2.5mm cable not affected by rads in use:
And not like this:
My apologies - I didn't spot the change in colour - I was too busy being distracted by the figures which I thought represented the currents flowing.No no they are not the same.
The first diagram shows the 2 rads drawing 5KW in total and the current is only flowing through the 4mm cable, not the 2.5mm cable hence why it's shown in black.
So if the TV is off what would be causing current to flow in the final segment?The second diagram shows the 2 rads drawing 5KW in total and the current is flowing through the 4mm cable, AND the 2.5mm one but as you can see, the telly is switched off!
I think it's great that you want to learn how things work, but if you are still at the stage where you don't understand the basics of electrical circuits well enough to know, without needing someone to confirm, that if there is no load then there will be no current then you really should do some studying which is properly structured, rather than asking random questions to try and eliminate the niggling things that you might think are all you need to clarify.I think diagram 1 is right and diagram 2 is wrong. All i need now is for someone to confirm.