Discussion in 'Electrics UK' started by Jupiter01, 23 Mar 2021.

  1. Jupiter01

    Jupiter01

    Joined:
    30 Mar 2015
    Messages:
    2,940
    Thanks Received:
    39
    Country:
    United Kingdom
    A friend of mine recently had an issue where the flat above his had a leak. This water eventually came through his ceiling and amongst other damage, it affected his light fitting which was quite close to the spot of the leak. The light was flickering when switched off at the wall switch. Switching the light on seemed fine but it was flicking when the switch was in the off position.

    I considered, switching off the lighting circuit at the board but all the lighting was being run from a single breaker. I assumed the issue was being caused by the live feed (presumably at the pendant) coming into contact with water. Does this sound plausible and what would be your advice in such a situation?

    Thanks in advance.
     
  2. Sponsored Links
  3. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,095
    Thanks Received:
    1,686
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    I have had this with LED lighting with no water leak, it was caused by the electronic switch, so I would try even if temporary swap the light switch.
     
    • Like Like x 1
  4. HERTS P&D

    HERTS P&D

    Joined:
    9 Apr 2010
    Messages:
    12,816
    Thanks Received:
    1,962
    Location:
    Hertfordshire
    Country:
    United Kingdom
    Call someone who knows what they are doing!

    Andy
     
    • Like Like x 1
  5. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,532
    Thanks Received:
    1,075
    Location:
    Dorset
    Country:
    United Kingdom
    If there is water running into a light fitting, that and maybe other circuits need turning off at the mains IMMEDIATELY.

    Then, someone competent needs to test that the effect wiring is completely dead, and set about drying out the wires and fittings.

    Some fittings need to be replaced, as the terminations can go black, which means poor contacts.

    Leaving the circuit on at the mains without ensuring the light fitting was dried out nicely was completely the wrong thing to do.
     
    • Like Like x 1
  6. Jupiter01

    Jupiter01

    Joined:
    30 Mar 2015
    Messages:
    2,940
    Thanks Received:
    39
    Country:
    United Kingdom
    Could water contact with the wiring cause this issue too? Seems a coincidence as there were no flicker issues prior to the water leak
     
  7. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,532
    Thanks Received:
    1,075
    Location:
    Dorset
    Country:
    United Kingdom
    It is likely that when the light switch was turned off, the water in the light was bridging between the switch live terminal and the permanent live terminal.
     
    • Thanks Thanks x 1
  8. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,095
    Thanks Received:
    1,686
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    I have all RCBO protection in my house, I also had water ingress and the RCBO did trip, on replacing the socket it was clear it had warped due to one assumes heat even with RCBO protection at 30 mA, so yes it does need items checking, and you want it done while fresh if for no other reason than claiming on the other flats insurance.
     
    • Thanks Thanks x 1
  9. Jupiter01

    Jupiter01

    Joined:
    30 Mar 2015
    Messages:
    2,940
    Thanks Received:
    39
    Country:
    United Kingdom
    Did the socket warp? Were the cables ok?
     
  10. Sponsored Links
  11. Jupiter01

    Jupiter01

    Joined:
    30 Mar 2015
    Messages:
    2,940
    Thanks Received:
    39
    Country:
    United Kingdom
    What’s the process for drying cables once the supply has been disconnected?
     
  12. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,532
    Thanks Received:
    1,075
    Location:
    Dorset
    Country:
    United Kingdom
    Usually with a kitchen towel to get the excess off, then judge if any more water will emerge from the ceiling.

    Turning the heat up can work if it seems really wet.

    But you need to check if the connections have been blackened.
     
    • Thanks Thanks x 1
  13. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,095
    Thanks Received:
    1,686
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    My cables were OK, needed to swap one light switch and one socket due to leak.
     
    • Like Like x 1
  14. Jupiter01

    Jupiter01

    Joined:
    30 Mar 2015
    Messages:
    2,940
    Thanks Received:
    39
    Country:
    United Kingdom
    Is this the connections to a fitting e.g. light, socket, etc.?

    Fo the cables themselves ever need replacing after water ingress?
     
  15. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    72,759
    Thanks Received:
    4,166
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    after turning off the electricity, puncture the ceiling with a skewer or similar so that any water can escape. Do this wherever you see damp patches, sagging plaster, or bubbles in paint or paper.

    It is easy to fill and redecorate a small skewer hole once the ceiling is dry.

    Put a bucket or other container under any drips.

    It is very convenient if you can make drain holes above sinks or baths so that any dripping water will go down the drain without damage.
     
    • Thanks Thanks x 1
  16. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,532
    Thanks Received:
    1,075
    Location:
    Dorset
    Country:
    United Kingdom

    Yes, a fitting that has got wet.

    The cables should be ok. The ends may go black. Cut the ends off and re-strip. If still black, rub them back to clean copper with some steel wire wool.
     