Fused Light Switch spurred from Mains Socket

Discussion in 'Electrics UK' started by meastwood, 8 Apr 2018.

  1. meastwood

    meastwood

    Joined:
    2 Sep 2017
    Messages:
    14
    Thanks Received:
    1
    Country:
    United Kingdom
    Hi there,

    I'm sure this has been answered several times already, but I'm trying to spur a fused switch from a mains socket to a light.

    From the little I have gathered so far, I have to make sure of the following:

    1. 2.5mm cable from socket to fused switch
    2. 1.5mm cable from fused switch to light
    3. Change fuse on switch to 5amp instead of 13amp
    Question:

    Do I need to spur onto an FCU and then from an FCU to an unfused light switch then to light?

    Or can I go directly from socket to fused switch to light?

    Many thanks in advance.
     
  2. Sponsored Links
  3. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,784
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    1. You should also check that the socket you are spurring from is not already a spur, unless it is a fused one, in which case fine.
    2. Or 1mm². It's no big deal - 1.5mm² will also be fine, and in fact is harder to break. Take no notice of anybody popping up who tries to tell you that using 1.5 will hasten the end of civilisation by wastefully using too much copper. Or quibbling that lights are also "mains".
    3. Yes.

    You can use the FCU as the switch for the lights if you want.

    Is the circuit RCD protected?

    You should be aware of the rules for where you may conceal cables. https://www.diynot.com/wiki/electrics:walls
     
    • Thanks Thanks x 1
  4. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    7,132
    Thanks Received:
    868
    Location:
    Dorset
    Country:
    United Kingdom
    To clarify what has already been told, if this is a 30 or 32amp ring circuit and the socket in question is an unfused SPUR, you would need to convert the socket to a 13amp FCU, then this will then supply both the socket and the 5amp switched FCU for the light.

    If the socket is fed directly from the ring circuit, or you have a 20amp radial circuit, then you should be able to omit the '13amp FCU'.

    Take no notice of anyone popping up who tries to tell you that there is no such thing as 5amp FCU, I have only written that to distinguish between the two FCUs.
     
  5. meastwood

    meastwood

    Joined:
    2 Sep 2017
    Messages:
    14
    Thanks Received:
    1
    Country:
    United Kingdom
    Thanks for the replies.

    The socket is unfused, but Pretty sure it’s on the main ring circuit as it’s a new build. It also has 2 wires going into the socket.

    Is there any other way of telling it’s not a spur? Is it worth doing a resistance test?

    Yes the circuit is RCD protected.



    Thanks.
     
  6. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    30,601
    Thanks Received:
    3,307
    Location:
    Retired to:
    Country:
    Portugal
    You need to switch off the power and remove the socket then disconnect the two Line(live) conductors (and Neutral) and see if there is continuity between them - because, if it is a ring, they will be connected together at the CU.

    Do you have a multimeter?
     
    • Thanks Thanks x 1
  7. meastwood

    meastwood

    Joined:
    2 Sep 2017
    Messages:
    14
    Thanks Received:
    1
    Country:
    United Kingdom
    Yes I’ve got a multimeter - so do I test live to live, neutral to neutral and earth to earth?
     
  8. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    30,601
    Thanks Received:
    3,307
    Location:
    Retired to:
    Country:
    Portugal
    Yes, that's right.
     
  9. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,784
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    At the main switch or RCD, not just the MCB for that circuit.
     
  10. Sponsored Links
  11. meastwood

    meastwood

    Joined:
    2 Sep 2017
    Messages:
    14
    Thanks Received:
    1
    Country:
    United Kingdom
    Thanks all - it is on main circuit - connectivity is there.

    My main problem now is I've got a flipping metal stud in between my socket and where I want to put the switch and light.

    Any ideas of running cables past a metal stud?

    Thanks!
     
  12. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    5,369
    Thanks Received:
    385
    Location:
    London
    Country:
    United Kingdom
    As has been stated you don't need 1.5 mm for a light, 1.0mm is fine, cheaper and saves the planets valuable resources of copper.
     
  13. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    18,764
    Thanks Received:
    1,877
    Location:
    Oxfordshire
    Country:
    United Kingdom
    :rolleyes:
     
  14. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,784
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    Go away, Winston - nobody wants to hear this nonsense ever again.
     
    • Like Like x 1
  15. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    5,369
    Thanks Received:
    385
    Location:
    London
    Country:
    United Kingdom
    What nonsense? It is very common for people to use oversize cable for lights. What is nonsense about correcting them?
     
  16. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,784
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    You is.
     
  17. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    22,271
    Thanks Received:
    2,080
    Location:
    Bedfordshire
    Country:
    United Kingdom
    The nonsense is when the corrector is incorrect
     
    Last edited: 9 Apr 2018