    Hi new here....

    We have a new build house and want to put the microwave in the kitchen cupboard there is a blank, and a fused spur that isolates the boiler in there I was going to tap off the fused spur to install new socket.

    However when I took the cover off the fused spur it’s only got 1.5mm on the feed to the fused spur.....

    Can I come off this fused spur to supply a single socket ?
     
    Last edited by a moderator: 20 Mar 2021
  2. Sponsored Links
  3. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,527
    Thanks Received:
    2,132
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Obviously you cannot connect to the load side of the fused spur. The fuse for the boiler will probably be the (required) 3amps, and that's too small!.
    You could spur from the supply side of the FCU, providing it is on a ring final, and not already a spur. How many wires are there in the supply side of the FCU in the live terminal? Post a photo if you not sure.
     
  4. Monkeeboy

    Monkeeboy

    Joined:
    20 Mar 2021
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    7B65B905-CFAB-483D-B4DA-BB946B0EB8D3.jpeg
     

    Attached Files:

  5. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,753
    Thanks Received:
    1,101
    Location:
    Dorset
    Country:
    United Kingdom
    What size circuit breaker at the consumer unit protects this circuit?

    You say the cable is 1.5mm2, it looks smaller to me - could it be 1.0mm2?
     
  6. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,527
    Thanks Received:
    2,132
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Yes looks like dedicated feed for the boiler. No chance you can use that.
    Is there another socket in the room that you could connect to?

    edit: I-spy another cable going east west through that back box. Looks bigger too. Where does that go to/ from?

    looks like there’s another accessory on the left hand side of the boiler switch. What is that?
     
  7. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,603
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    One could, IF that were the case, but ....
    ... so I agree with what you have said subsequently.

    Kind Regards, John
     
  8. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,390
    Thanks Received:
    4,194
    Location:
    Retired to:
    Country:
    Portugal
    If it IS 1.5mm² Method C, then a 3A fuse for the boiler and 13A fuse in a plug in a single socket would be alright - wouldn't it?

    Or shall we argue that someone in the future might swap the socket for a Hadron Collider?
     
    • Thanks Thanks x 1
    • Like Like x 1
  9. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,603
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    In terms of Cable CCC (hence electrical considerations) it certainly would be OK (so long as the fuse in the FCU continues to be 3A).

    I imagine that the main imagined 'issue' likely to be cited by some (many?) is presumably Appendix 15, which that some/many will probably say say 'prohibits' (not that it can/could!) two or more 'anythings' being supplied by an unfused spur from a ringFC (even, I presume, if those somethings were both FCUs with 1A fuses).

    Kind Regards, John
     
  10. Sponsored Links
  11. Monkeeboy

    Monkeeboy

    Joined:
    20 Mar 2021
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    AA1452A3-F357-45FC-ABBE-AA6F8E21ED84.jpeg
     
  12. Monkeeboy

    Monkeeboy

    Joined:
    20 Mar 2021
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    The fused spur has a independent feed as mentioned above I haven't checked the size of the fuse I would imagine 3amp.

    The twin & earth running east to west pic 1....Terminates behind the blank pic 2 combining the two flex cables coming down from the boiler, then loops back to the outgoing side supply from the fused spare, which has me baffled and this is also not 2.5mm

    We have a double socket to the right low level on the wall though it’s looking like an unsightly extension out of the side of the Cupboard low level about a half a metre away and plugging in there which we wanted to avoid as it’s opposite the entrance to the kitchen and the first thing you will see ‍♂️
     
  13. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,543
    Thanks Received:
    1,742
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    Have you found the fuse/MCB/RCBO that the FCU is fed from? In my house I have 14 RCBO's only 4 are ring finals, 3 are lights, the rest are supplying one item and it may be the same with your house.

    So the instructions will change depending on the supply, 16 amp, 20 amp, 25 and or 32 amp.
     
  14. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    74,126
    Thanks Received:
    4,282
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    nasty job.
     
  15. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    37,119
    Thanks Received:
    1,288
    Country:
    United Kingdom
    :ROFLMAO::ROFLMAO::ROFLMAO:
     
  16. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,527
    Thanks Received:
    2,132
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Would that need a Fusion Connection Unit?
     
    • Like Like x 3
  17. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,603
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    :) :)

    ... maybe only a JB! As EFLI was implying, some of these people who think that electrical installations have to be designed with "any possible future idiocy in mind" should presumably be concerned that any accessory on any circuit could, in the future, be replaced with a hard-wired connection to an inappropriate load - so, they should be 'concerned' about an unfused spur from a RingFC supplying just one single socket (which no-one would claim was 'non-compliant) with, say, a hard-wired connection to a shower.

    Kind Regards, John
     
  18. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page