Hello.
Could do with some advice please!
Have just had two timber buildings added close to house.
Initially planned on using spare way on RCD side of CU with 20A MCB to feed new 45A 2-way 30mA RCD unit via 4m of 4mm SWA T+E, and from 16A MCB there max 10m of 2.5 SWA T+E into second building and second RCD 2-way unit.
Cables laid already. No pipework to bond, armour to be bonded at glands at all ends via earth core back to main CU.
At this stage only nominal loads expected (couple of striplights and 4 sockets in each building, running tool chargers, occasional garden tools etc).
Since laying cables I have had to move leaky cooker circuit to non-RCD side of CU, leaving a second spare way available on that side. As nothing is terminated yet I still have sufficient cable to run the 2.5 straight to the 2nd spare way if this is preferable to the above, though it will be more hassle and I'll have no spare ways left should I need one.
Should I do this, or is the above adequate and safe?
Thanks for any advice.
Could do with some advice please!
Have just had two timber buildings added close to house.
Initially planned on using spare way on RCD side of CU with 20A MCB to feed new 45A 2-way 30mA RCD unit via 4m of 4mm SWA T+E, and from 16A MCB there max 10m of 2.5 SWA T+E into second building and second RCD 2-way unit.
Cables laid already. No pipework to bond, armour to be bonded at glands at all ends via earth core back to main CU.
At this stage only nominal loads expected (couple of striplights and 4 sockets in each building, running tool chargers, occasional garden tools etc).
Since laying cables I have had to move leaky cooker circuit to non-RCD side of CU, leaving a second spare way available on that side. As nothing is terminated yet I still have sufficient cable to run the 2.5 straight to the 2nd spare way if this is preferable to the above, though it will be more hassle and I'll have no spare ways left should I need one.
Should I do this, or is the above adequate and safe?
Thanks for any advice.