Hi,

New to forum, but not DIY however, Electricity is something I rarley deal with other than changing switches for dimmers, light fitting change or the odd double socket spur.

I apologise in advance as this may be a long initial posting - more like bedtime reading! :)

I'm looking to run mains into my 'virgin' concrete section garage (pitched not flat roof) using SWA from main CU to 'garage' CU (MK garage kit RCD [40A 30mA] & 2 X MCBs [16A & 6A], IP65 rated).

From having browsed some of the previous threads, I'm assuming that 6mm 3 core SWA will suffice to feed the garage CU, the armour being terminated [earthed] at house CU end only?. As garage CU is also Poly Carbonate / plastic or similar how / where should the armour be terminated for 'best practice'?

What size MCB should I use in the Main CU to provide for the garage?
I have spare postions.

An underground plastic pipe (25mm water type) exists from near CU location to garage which currently has an extension lead run through to provide temp power. Straight line distance CU to garage 3M approx.

I will also be running in a telephone type cable to extend my alarm system to the garage, can this be run in same pipe?

The garage is / will be a workshop more than some where to store the car (if only I had the room!). Therefore I'm likely to be running power tools eg drills, bench grinders etc as well as having batt chargers etc perm powered. I may also be using arc welding equipment from time to time.
With this in mind I'm planning on installing 4/6 double sockets on a ring, and cabling out in 2.5mm SWA rather than T&E for safety reasons, from the purlings down to the sockets. Am I OK so far or is the SWA overkill for sockets?
Any tips on sockets and their mounting? I was contemplating using steel sockets and screwing direct to concrete rib, 'gently' using SDS drill and rawl plugs (have done drilling before!). Any tips on type of flange to use if at all on the sockets?

I'm unsure what to do re lighting, both type and location, as the roof space is limited as I have wood, pipes, fishing rods, boards etc up there already. I'd thought about using conventional tube lighting with perhaps 2 circuits front / rear of garage (22 ft X 14 ft), switching both from either end of garage as it also has a side door.
Are reinforced enclosures available to prevent tubes being accidentally damaged? 'Normal' Plastic shade type fittings seem a little flimsy for this purpose. I'd though about bulkhead type lights but don't think they'd provide enough illumination without it looking like a string of fairy lights. Any suggestions?
I'm assuming a ring of T&E for the lighting circuits will be ok, 4 core for swicthing but not sure about conductor size.

To the garden - I want to install a spur from the garage to an IP56 switch for a water pump, then continuing on to 2 X single IP56 sockets fastened (sds drill / screwed) to firmly concreted in fence posts at side of small patio area.
The entire run will be paved over, only socket feeds will be above ground from tees below flags. This I'm intending running in SWA 2.5mm 3 core DIG (direct in ground). Any tips on type of flange to use on the IP56 sockets and type on 'tee' junction boxes to use u/g?

I'm also installing a Ring LV lighting system running from transformers which will be plugged into remote controlled sockets located in the garage. The instructions for this lighting says it should 'not be run next to mains' which causes me a problem, how far should these be apart? as the run for the sockets and the LV lighting will be the same from the garage to the end of the socket spur.

Could I use same trench for both?, mains in the bottom covered with warning tape then a layer of soil/hardcore, then plastic conduit above it carrying the LV?

I'm assuming that the mains side of this is reportable?, but don't know how to go about doing so, or how much of the work I am 'legally' allowed to do. I want to do as much as possible myself due to costs, my labour is free! and perhaps call in a sparky to check and connect at the main CU, is this feasible?

Any suggestions or tips would be very much appreciated if I need to change spec on anything please let me know.

Thanks.
 
Sponsored Links
Terminate the armour at both ends. If you have no extraneous conductive parts in the garage the earth can be exported, and earthing both ends means the armour is well earthed.

Stop going on about ring circuits. :LOL: They aren't nessecary, especially with a 16 amp MCB. Lighting is never done in a ring anyway.Because you have 6mm cable, you can provide a 32 amp radial circuit in the garage, for the sockets. Sounds like you will need it, with the welder.

For a 5m run, 6mm SWA can be protected by a 40 amp MCB, non-RCD protected. You only need one RCD, in the garage.

SWA in the garage is fair enough, if you want the work. Probably the best way to offer protection to the cables as a DIYer.

Fluorescents can take a surprising amount of force before they shatter - i bashed my head on some quite a bit where i worked in a shop with very low ceilings in the cellar. Though I might just have a soft head :LOL:

anti corrosive fluorescent fittings- TWIN
anti corrosive fluorescent fittings - SINGLE

Of the two pages above, get the ones with high frequency ballasts, since this will eliminate strobing caused by flickering of the lights. Strobing would make your power tools appear stationery, when they are moving.
 
Hi Steve,

Thanks for clearing up the ring / radial error, hadn't actually meant to type ring for lighting - my fault for not proof reading before posting.

Am I best off going for steel sockets? anyone?

Also is there a recommended minimum distance between mains and LV?
If so I may have to re-think my layout.

Any other advice re this or original posting appreciated

Cheers.
 
Sponsored Links
Metaclad sockets are advisable, but not strictly nessecary. Depends what you'll be doing in there i guess.

Have you added more info to the original post? Please dont do this!

I would also rethink the garage CU idea. A 4-way CU would be far better in a "workshop" type place, as it will give you far more scope to upgrade in future. This is my shed CU, note it has 2 spare ways, and only the sockets are RCD protected. This lights stay on when the sockets trip their RCD.
DSC00839.jpg


Note that according to the regulations, "Only sockets that can reasonably be expected to supply outdoor appliances must be RCD protected" This is the ONLY provision for RCD requirement in the current regs.

For 5 metres of the stuff it wont cost you must to put in 10mm² SWA to supply the garage.


You cant bury junction boxes underground, unless they are resin filled. The best way to do outdoor JBs is to hammer in a treated board into the ground, and use this to mount your junction box on, this can be out of sight if you wish, though the runs of cable between JBs should be straight, so its pretty obvious.

Use the same trench if you want, I cant see there being a lot of harm in having LV alongside ELV (230V = LV, 12V = ELV). After all, the power companis have 11KV running over 400V all the time, uninsulated!
 