glow-worm 30cxi problems

Joined
26 Sep 2012
Messages
1
Reaction score
0
Location
Yorkshire
Country
United Kingdom
my glow-worm 30cxi boiler keeps losing pressure everytime heating is on water is escaping through relief valve and i have had new expansion chamber 12 engineers have tried but still no good please help me
 
Sponsored Links
Like the above said check EV should have 0.7bar(10psi) and after that the most common one is the hose from the top of the pump block to the EV will be choked up completely.
 