Has anyone run a radial main in 4mm2 T&E?

Joined
22 Jun 2006
Messages
251
Reaction score
1
Location
London
Country
United Kingdom
Has anyone run a radial main (supplying kitchen sockets and appliances) in 4mm2 T&E? Do common accessories (double sockets, fused connection units, etc) accommodate this size of cable OK?
 
BS1363 requires that they accept 3x2.5mm² or 2x4mm², some go beyond this, and you can terminate 2x6mm² in MK stuff (but that is a tight fit and I dare say you'd need a deep box)
 
Hi, I've used 6mm with Crabtree sockets without problem. As Adam said, the size of the backbox is the limiter as it's not that easy to bend. HTH
 
I do it often in commercial kitchens - 2 sockets per circuit, so one has to loop in/out. I use standard 25mm boxes most of the time for flushed ones, and use MK MCO fronts.

It's the sensible way to go :wink:
 
Thanks for that, guys. I got the 4mm2 T&E today and it looks fairly workable. I'm using 35mm back boxes and, as it's a radial, will only have one coming in and one going out on everything except the last one in the chain.
 
Why not, for the sake of it put in an extra cable and make it a ring?
 
newspark_paul said:
Why would you opt for a ring over a radial. Apart from the smaller cable.
Well - let's see.

More complicated to test.
Problems and possibly danger with branches added in the future.
Breaches to the integrity of the ring, and therefore safety, not apparent via non-working sockets.
The need to specially craft wiring regulations to allow the use of 2.5mm² cable on 30/32A protective devices.

There may be more reasons, but I can't think of any right now....
 
I always find numpties extending a 4mm radial with 2.5....strictly speaking it's no different from spuring from a ring.....but it's wrong :?

Rings are ok for domestics, 4mm is fairly expensive. I still use rings for domestics, but for commercials, I always opt for radials.
 
I have to run the cable through very restricted space in a loft, so I reckoned running one cable would be less work than two! Also, all the accessories will be behind tiles, so there will be little likelyhood of spurs being added.

Anyway, I haven't used 4mm2 before, so it'll be a new experience...
 
use the same calcs as you do with 2.5 (66% each leg for current etc)
 
You need to get up to speed on changes to the wiring regs - that's no longer in there... :wink:

I'm not saying that it's wrong, but it is no longer a compliant method, so you're into departures from BS7671, and possibly trying to persuade a numpty inspector at some point of the validity of your electrical engineering calculations....
 
and its not as if there is really much point in having a socket circuit over 32A anyway at least not in a domestic situation.
 