I suspect that he was intending to use the (1.5mm²) L or N conductor, not the CPC, of 1.5mm² T+E.The CPC on 1.5mm T&E will be 1.0mm not 1.5mm. ...
Edit: too slow again!
Kind Regards, John
That's understandable, but not what I was suggesting, as I stated dictated be the plate being used.Fair enough. I was actually (unnecessarily) thinking about accessories more generally (which don't all have earth terminals, hence don't all have earthed screws).
I am and your not the only one who prefers that additional protection, but it is not a requirement, although good practise.Having said that, as you will be aware, I am personally not all that happy with reliance on faceplate screws to earth a metal backbox.
No, one should not be removing covers on live accessories, but we know this happens!Although one obviously should not be removing a faceplate and pulling it forward whilst a circuit is live,
I understand and agree with your concerns, and on metallic plates I practise the methods you do, even though it is still not a requirement when solid/fixed lugs are present on metallic back boxes. And as a primary precaution, advocate isolation and proving dead before meddling.if one does that and the pulling forward causes the live conductor to become disconnected from the accessory (which most of us have seen happen), that lose L conductor could come in contact with the (unearthed) backbox, leaving one confronted by a lot of live metal. For that reason, I personally always have an explicit (wired) earth/CPC connection to any metal backbox.
Fair enough, but the theoretical risk I was describing exists just as much with a plastic plate as a metal one, so I'm not sure why you only do it with metal plates!I understand and agree with your concerns, and on metallic plates I practise the methods you do, even though it is still not a requirement when solid/fixed lugs are present on metallic back boxes.if one does that and the pulling forward causes the live conductor to become disconnected from the accessory (which most of us have seen happen), that lose L conductor could come in contact with the (unearthed) backbox, leaving one confronted by a lot of live metal. For that reason, I personally always have an explicit (wired) earth/CPC connection to any metal backbox. As for 'not being required', that's obviously true - but, although the regs often seem to be over-cautious, this is, IMO, a contrary example of them being somewhat 'under-cautious' (at least, less cautious than I personally am)!
Of course, but we know it happens - and dare I suggest that most of us have probably done it in our time (particularly with plastic plates)?!And as a primary precaution, advocate isolation and proving dead before meddling.
i need about 5cm of this i think (should i do it at all)
http://www.screwfix.com/p/conduit-wiring-cable-6491x-1-core-1-5mm-x-100m-green-yellow/61678[/QUOTE]
But that's a 100metre roll!!
Surely you have a bit of unused cable hanging around the place, somewhere??. Pop up the council tip, you'll find a bit for free, or dont bother at all.
... dare I suggest that most of us have probably done it in our time
A cheaper alternative is a peice of 1.5 3 core flex usually sold by the metre and strip the earth out, even salvage from a dumped appliance like a washing machine
It could be a potentially major issue if there is only one earth wire. However, there's no point in crossing that bridge unless you come to it. If (as is probably unlikely) you find that there is only one earth wire, let us know and then we can discuss the situation and advise you accordingly.... Just going back to this picture , i am at work so cant check and i cant recall , but apparently there should be TWO earth wires in the green sleeve , what would be the issue if there wasnt ?