Hob Installation
3 Jan 2006
Durham
i am changing my electric hob but have a question regarding the wiring. My old hob had 6mm cable going to it, however 6mm does not seem to fit the new hob. Well it will but because it has links in, the 6mm and the link will not fit in the same connection block.
On the installation instruction for electrical it has the following:
220-240V H05V2V2-F 2.5mm
Does this mean i can use twin and earth 2.5mm or is this a heat resistant cable but still 2.5mm?
any help would be gratefull
Ideally you would use 2.5mmsq Butyl heat resistant flex. If the cable to your old hob was 6mmsq this suggests the protective fuse/MCB rating for the hob circuit in your consumer unit is probably a little high. You might want to consider the power requirements of the new hob and possibly downrate the protective device before putting a length of 2.5 in the circuit.
The cooker circuit is on a 32A MCB, however the oven is connected also on this circuit via a FCU spurred off the hob terminal (not sure of its technical name).
Therefore there is 6mm going from consumer unit to cooker switch. 6mm going from cooker switch to hob terminal below worktop. 2.5mm spur to a FCU from the hob terminal which the oven is connected to. Then there is 6mm coming from the hob terminal to be connected to the hob, which im not going to replace with the cable you mentioned and connect to the hob.
Does that sound about right? Or will i have to look at the current draw etc?