Hi, I could do with a bit of help regarding a kitchen upgrade.Having just re-fitted my kitchen, I installed 10mm2 T&E from the consumer unit to the above worksurface switch box, leaving sufficient T&E to run from the switch to what I presumed would be a under- worktop connection box. However my sparky decided that, as at that time, I was only running a 6.5 Kw hob , and a low power oven running of the ring main, I would only need 6mm2 T&E from the switch to the hob!(Without a connection box) Now, I want to fit a 3.6 Kw oven under the hob giving me a total load of 10.1Kw
and i'm a little uncertain of the best way to do it. My original plan was to fit a surface mounted connection box under the work surface and connect both the hob and the oven to that, fitting a 45 amp mcb in the consumer unit. However will this short piece of 6mm2 (30 cm buried in conduit,plaster and tiled) prevent me from doing this and if so, is there an easy solution? With thanks for looking