1. Turn CH and HW OFF at programmer - done
2. Set CH and HW stats to minimum - done
The valve is in the default, unpowered, state. Port B (cylinder) is open
3. Turn HW ON at prog. (Boiler stays OFF) - boiler stayed off
4. Turn HW stat to Max (Boiler turns ON) - boiler turned on
Pipe to cylinder gets hot - pipe got hot
5. Turn HW stat to Min (Boiler turns OFF) - boiler turned off
Pipe to cylinder cools - yes it did
HW, on its own works. Step 5 should put 240V on the grey wire from the cylinder stat Sat terminal.
6. Turn CH ON at prog. (Boiler stays OFF) - yes, stayed off
7. Turn CH stat to Max (Boiler turns ON) - boiler did not turn on
Pipe to rads gets hot - no
The CH stat should apply 240V to the valve white wire. This, and the 240V on the grey wire should mean that the valve opens port A only (radiators).
Failure means:
1. Faulty valve (sticking or motor shot)
2. Voltage on grey but not on white
(Voltage on white but not grey would put valve in mid-position - CH and HW ON)
8. Turn HW stat to Max (Boiler stays ON) - boiler turned on
Pipe to rads stays hot; pipe to cylinder gets hot - pipe to rads stayed cold, pipe to cylinder got hot
It should have gone to mid-position (both HW and CH on0 but has reverted to the HW only position due to the above faults
9. Turn HW OFF (Boiler stays ON) - boiler went off
Pipe to rads stays hot; pipe to cylinder cools down - pipe to rads stayed cold, pipe to cylinder cooled down
HW OFF should have applied 240V to valve grey.
I left the controls at the last settings above and the boiler fired up after about 30 mins wait. Rads now nice and warm. The pipe to the HW cylinder has also got very hot though even though the HW was still off at the programmer.
So the valve had gone to mid position.
First thing to check is if the valve is sticking
Turn power off
Remove the actuator (Blue box)
Check that the spindle can be turned easily by hand (20 degrees only).
Replace actuator.
Move the lever at the end from Auto to Man. There should be resistance and the lever should return to Auto when released.
If that doesn't reveal any problems, more tests will be necessary. But that will be difficult due to the unorthodox wiring.