Most problems can be found with a little more diagnosis...
These questions are asked as a double check so don't take offence if they seem simple or obvious.
1. when the flow pipe from the boiler gets hot, does it get hot on just one side of the pump or not at all? There shouldn't be any form of valve inbetween the two except the one connected to the pump for isolation purposes.
2. If it does reach this valve, is the valve open? along with the valve on the opposite side of the pump?
3. the next ones obvious, but it's friday after all... is the pump flowing the correct direction? There will be an arrow stamped into the bottom of the casing.
4. was the pump bled also? they don't normally whirr to loud when full of water.
If all of these are ok, and you're still not getting hot water, the only other thing I can think of is to check the hot water is not venting straight into the F&E from the boiler pump?
Hope some of it helps,
Cheers.