hot water only pipes banging ! turn on c/heating stops this

Joined
21 Apr 2005
Messages
7
Reaction score
0
Location
Hampshire
Country
United Kingdom
Hi
I have a potterton profile 50l boiler.

When i turn on the hot water only - after 5 minutes the pipes start banging really loudly increasing in volume !!!

I f i then turn on the central heating the noise stops straight way !

Can anyone explain 1. why it stops the noise ?
2. What i can do to fix this problem ?

thanks

Carl.
 
Sponsored Links
1.)For some reason the water isnt moving fast enough through the boiler when on HW only. Could be sludge, blockage, knackered diverter or zone valve.[or maladjusted balancing valve causing a slightly different scenario]
When the CH goes on the pump drags the water through faster thus stopping the 'kettling' thats going on in your boiler