Oven - 3400W, 1.5-2.5mm cable, can be 13A plug'd if need be
Hob - 6000W, 4-6mm cable, 45A
I replaced the Oven about 1 yr ago but hob has sat in box (many reasons why hob not fitted at same time) but now its going to be fitted.
Behind the oven are 2x 13A switches (not sockets), in vertical placement one directly above the other. One wired to the Cooker Switch above the counter (big Red switch with light), the other into god-knows where but cabling is fairly chunky.
At your main fuse board is all this switching wired as 1 cct and what is the amp rating ?
For you to do as you intend, if they are all on once circuit the potential load (no diversity considered) is 9400w /230v = 40 amp.
So has the circuit been fused at 45 amp ?
Since all switches for isolation (say a chip pan fire) need to be accessible you need to move the switches.
So something such as 2 x
http://www.tlc-direct.co.uk/Products/MKK5105.html
Those are 32A MK switches, the 45A feed from the CU would terminate in 1 and then be extended to the other forming a 2 position radial. You would then require 2 x 4mm feeder cables from the switches to the appliances.
There's a scheme called SELECT in Edinburgh, which is the Scots part P and you will require a spark for certification.