I had the house rewired a few years back and I remember the electrician used 1.5mm cable for the lighting circuits - is that not right?[/quote said:It is not wrong and not necessary. 1.0mm is OK for lighting on a 6A MCB.
The answer to your original question is normally 10. This assumes each light point consumes approx 100W.

314.1 Every installation shall be divided into circuits, as necessary, to:
(i) avoid hazards and minimize inconvenience in the event of a fault
(ii) facilitate safe inspection, testing and maintenance (see also Section 537)
(iii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents produced by equipment in normal operation
(v) mitigate the effects of electromagnetic interferences (EMI)
(vi) prevent the indirect energizing of a circuit intended to be isolated.

AFAIAA, the regs are pretty silent on the matter of ratings/protection of accessories - their main interest is in protection of the cables. A problem could, of course, arise if the manufacturer's instructions for, say, a "6A rose" say something about a 6A OPD - in which case use of a 10A OPD could become non-compliant with the regs.Sockets are effectively used as junction boxes on circuits and they have a face value rating of 13A, yet the CPD is anything up to 32A. ... Roses on lighting circuits are the same, surely? You could have a 6A rose on a 10A breaker without contravening the regs?