Will they sign it all off for you , if you do that ?My plan is now to run cables etc to appropriate positions and have a qualified guy do the connections.
Will they sign it all off for you , if you do that ?My plan is now to run cables etc to appropriate positions and have a qualified guy do the connections.
Advice - not MIs then.I understand that, but I came across (I think
On AO) a 13A oven, where the advice was hard wired.
Apart from the above.In truth, it does not matter a great deal,
Up to you.I suppose.Plug in would be easier as the Sparks can do their thing and leave me to fit the oven.
Yes, way over the top and unnecessary.My plan is now to run cables etc to appropriate positions and have a qualified guy do the connections.
Given the circs, is it fair to think a new CB and 3 radials (I assume that is what he meant) a bit OTT?
Surely fitting one circuit with three single or two dual cooker outlets will be quicker.I know that I could go back and talk about it, but I don’t want to waste his time - and I have plenty of time in my hands to do the grunt work.
The main reason for inviting a firm to quote was for a quicker install time to minimise kitchen down time.
I would hardly classify those as problems Eric! Much of it would similarly apply to Radials too to some degree.So the appendix to BS 7671 warns about the problems with ring finals, note we don't have the same problem with radials.
There was an article in Wiring Matters a few years back that seemed to conclude they did comply if just one front end RCD there ditto two RCD.And being cheap skates, we wanted to try and get away with using just two RCD's, today we realise that did not really comply
Yup I`m pretty happy with that too.Advice - not MIs then.
It would be better not to have an oven or two on the socket circuit but there is no reason not to have a socket or two on the cooker circuit.
Then there is the fact that there will probably be a cooker switch so I would like it to switch all the cooking appliances including a hood but that is just my preference.
Apart from the above.
Up to you.
Yes, way over the top and unnecessary.
Surely fitting one circuit with three single or two dual cooker outlets will be quicker.
Yes you must ask, they might not agree, I`ve agreed with time served qualified sparks then regretted the hassle but with "ordinary people" the chances of hassle is far greater surely?Will they sign it all off for you , if you do that ?
Yup I`m pretty happy with that too.

I have an RCD incomer inherited when we bought the house.In fact nearly all were one RCD - I am a front-ender I will readily admit to!
The hob alone is 7.2Kw.You could put the ovens on with the Hob most probably and you will probably also get away with a 32 amp instead of a 40 amp.

Yes diversity, the hob works out to roughly 16 amps ish.The hob alone is 7.2Kw.
Are you saying that based on diversity factors?
However, it will be less than that when paired with two ovens.Yes diversity, the hob works out to roughly 16 amps ish.

Oh yeahHowever, it will be less than that when paired with two ovens.
Say the two ovens were each 3.6kW - also 7.2kW.
14.4kW after diversity is 25A; half of which is 12.25A.
However, it will be less than that when paired with two ovens.
Say the two ovens were each 3.6kW - also 7.2kW.
14.4kW after diversity is 25A; half of which is 12.25A.