How to joint?

Discussion in 'Electrics UK' started by OxiaUK, 17 Mar 2021.

  1. OxiaUK

    OxiaUK

    Joined:
    9 Feb 2014
    Messages:
    64
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    This is only for info as its something ive wanted to know for a while.

    if you have a 10mm cable and you want to joint it (for example maintenance free) how would you do this?

    most connectors only go up to 6mm..

    and to make it more fun, how would you join a 10mm to a 6mm if you ever needed to and again make it maintenance free?

    Thanks
     
  2. Sponsored Links
  3. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,485
    Thanks Received:
    4,208
    Location:
    Retired to:
    Country:
    Portugal
    Plenty of large junction boxes but not sure any are MF.
     
  4. OxiaUK

    OxiaUK

    Joined:
    9 Feb 2014
    Messages:
    64
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    Thats my point... i dont see how your supposed to do it if you REALLY needed to and keep in safe and to regs.
     
  5. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,937
    Thanks Received:
    1,991
    Location:
    Poole, Dorset
    Country:
    United Kingdom
  6. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,648
    Thanks Received:
    1,748
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    [​IMG]I would use a set of these, since I have a set, but to be frank they do not work that well on 10 mm² when I wanted to extend cables I did buy a set for 10 and 16 mm which were much smaller and did a better job, there are both shrink sleeve and epoxy resin joint kits.
     
  7. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,674
    Thanks Received:
    3,191
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    As has been said an implied, even if there aren't 'MF' junction boxes available for large cable sizes (**), you still have a choice of crimping (various options available), soldering, brazing etc. all of which (with appropriate insulation) would be compliant with regs.

    ** I'm not sure about the 'bureaucratic' situation as regards compliance with Standards that would satisfy BS7671, but is it not the case that joints using non-screwed terminals (and hence essentially the same as the 'MF' JBs we know and love) have for a long time been used in industrial (and perhaps even electricity distribution) industries for very large conductors?

    Kind Regards, John
     
  8. bsr

    bsr

    Joined:
    5 Aug 2008
    Messages:
    591
    Thanks Received:
    53
    Location:
    Gloucestershire
    Country:
    United Kingdom
  9. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,674
    Thanks Received:
    3,191
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    They would certainly be difficult to 'maintain' :)
    Yes, I believe so.

    Kind Regards, John
     
  10. Sponsored Links
  11. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,648
    Thanks Received:
    1,748
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    Cores normally crimped, the earth often a scroll which presses a braid onto the SWA with a former underneath the SWA to hold it firm. But since the whole thing is filled with epoxy resin even if screw terminals used they can't come loose.
     
  12. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,674
    Thanks Received:
    3,191
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    The screws couldn't literally 'come loose' (i.e. rotate in their threads) but the actual electrical connection presumably could - e.g. due to 'creep' (maybe due to thermal cycling) in the material of the conductor(s)?

    Kind Regards, John
     
    • Like Like x 1
  13. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,648
    Thanks Received:
    1,748
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    But the same can happen in a crimped joint, so there is no difference be it crimped or screwed. In the main a screwed joint will use Alan keys or other method where a set torque which is quite high can be applied. I would agree with the shrink sleeve type really does need to be crimped, but the pour in epoxy resin type, it really does not matter.
     
  14. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,674
    Thanks Received:
    3,191
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Are you suggest that we should be allowed to pour resin (or, indeed, just use thread locking fluid) into a standard screw-terminal (non-'MF') JB and then treat it as 'maintenance-free'?

    Kind Regards, John
     
  15. davelx

    davelx

    Joined:
    26 Sep 2006
    Messages:
    1,929
    Thanks Received:
    171
    Location:
    London
    Country:
    United Kingdom
    I think I'd call that "non-maintainable" ☺
     
  16. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,674
    Thanks Received:
    3,191
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Indeed ... as I previously said about 'resin joints' in general...
    Kind Regards, John
     
  17. OxiaUK

    OxiaUK

    Joined:
    9 Feb 2014
    Messages:
    64
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    Thanks for all your replies, some interesting points here. How do you joint say a 10mm cable to a 6mm cable? surely you cant crimp a 6mm cable in to a 10mm uninsulated crimp joint?
     