• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

IDEAL ISAR HE24

Joined
9 Jun 2007
Messages
75
Reaction score
0
Location
Manchester
Country
United Kingdom
just been called out to an ideal isar 24he that had no hot water.
when arrived pressure at zero and told not worked for a couple of days ( hasnt had heating on due to warm weather..)

no lights on control panel, repressurised. no change

electricity at mains and getting to pcb, on off switch is electrically sound, no electricity at fan when 'calling for heat'

new pcb?
 
Didn't you diagnose the fault and repair it when on site?

Tony
 
no. surprisingly given the 24 hr shopping culture all the local factors were closed at 8 oclock on a wednesday night.
 
Bet its the PCB. I speak as an owner of an ISAR, not as a plumber. Been thru 3 PCBs in 2 years. Changing the PCB is all the Ideal engineer would do anyway! :D
 
PCB if everything is dead after the mains input to the board. Have you checked the fuse on the right side of the board?
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top