This is what the 13th Edition from 1st September 1955 has to say about "spurs".
Regulation 114 B (ii)
When spurs supplying outlying socket-outlets are connected to a ring circuit, not more than two socket-outlets or one fixed appliance shall be fed from each, and not more than half the number of points installed may be served by spurs.
Spurs shall be connected to a ring circuit in socket outlets or in suitable joint- or junction-boxes.
The conductors forming the ring circuit shall either be unbroken where they pass through socket-outlets or joint- or junction-boxes, or, alternatively, if the conductors are cut, the electrical continuity of the ring circuit shall be ensured by joints complying with the requirements of Regulation 208.
Regulation 208 (A).
Where joints in cables are required, they shall be mechanically and electrically sound and, except in buried cables, they shall be accessible for inspection. They shall be made either by soldering or by means of mechanical clamps which shall securely retain all the wires of the conductors.
NOTE.-- The resistance of a jointed conductor should not exceed that of a similar unjointed conductor.
Notice that for Reg 114, there are no fused spurs, no allowance for connecting unfused spurs at the origin of the circuit and only half the number of points may be spurs.
Regulation 208 (A).