Hi, thought to share electrical hook up issue today. I am finishing a garden workshop and power hook up for a friend. As I am not a certified electrician design was discussed and OK,d with my certified electrical tester.
Previous jobs done for various garages and workshops and signed off no problem with test cert provided
What threw me today when testing was 240v OK at main board mcd and 240v at shed consumer inlet on no load. However when switching on lighting and power circuits the voltage dropped to 120v and 75v.
After checking all external wiring continuity and isolation still problems. Then isolated everything and went home to think.
Looking at the existing house consumer unit photos noticed that I had connected the neutral to the protected neutral and not the unprotected neutral . Breaker is on the unprotected side.
Tomorrow will wire correctly and going forward will probably leave final board connection to the experts as I have done in previous jobs. No doubt I will in for a dressing down by my approved electrician.
Suitably humbled.
PeterC
 
Sponsored Links
Hi RCCB on house protected side did trip when I powered up the external circuits and at some points when checking for 240V at various parts of the external sub dist board.
 
Sponsored Links
Many moons ago, I went to this issue.

 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top