Guess The Fault Competition

Joined
11 Jan 2004
Messages
42,722
Reaction score
2,630
Country
United Kingdom
Today I visited a property.

The customer was complaining of voltage drop when a hefty appliance was used on the ground floor ring final.

He said that fluorescent lights would dim & appliances with motors would slow down.

I plugged my trusty Alphatek into the cooker control unit & it read 237V. Fair enough.

Then I asked the customer to plug a kettle into the GF RF & switch on.

Sure enough, the voltage plummeted to 199V.

What fault did I find?

;)
 
Sponsored Links
Sponsored Links
aA 100kw Kettle with a 15,000litre capacity (big tea drinkers living downstairs) :LOL:
 
What I actually found was two problems.

There's a bit of a clue....
 
Two loose tails? :LOL:

OK - maybe the sockets were wired off the lighting circuit and had a solid metal link in instead of a fuse?
 
I'm thinking some weird F'ed up polarity reversal plus neutral fault somewhere that we'd never guess in a billion years.

I had a feeling this would be a double, the best ones always are.
 
N>E fault on kettle

L&N reversed at incommer

Zs 3.29 ohms at the socket
 
Problem with tails connection into main switch or main switch on to busbar/outgoing N link?? (wrong side of clamp/s)
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top