    I have just finished a 2 storey and a single storey extension. I calculated the BTU requirements for radiators. In my kitchen/family room there wasn't sufficient wall space for traditional rads so I had to buy the expensive vertical ones. I went a little over with the BTU but the room is still not hot enough. The rads get screaming hot on the surface all over but they do not live up to their btu ratings. I think that due to the vertical nature and the lack of fins you get in a type 21 or 22 radiator that they are just not that great.

    Is anyone aware of any "fins" you can get to add to rads? mine are both double column so I could get some fins in between if anyone sold them.
     
  2. Sponsored Links
  3. foxhole

    foxhole

    Joined:
    14 Mar 2006
    Messages:
    15,693
    Thanks Received:
    1,725
    Location:
    Kent
    Country:
    United Kingdom
    Have they been installed correctly many vertical rads are designed to be horizontal and for vertical use have internal knockout section which has to be removed to give correct flow .
     
  4. needmorstuff

    needmorstuff

    Joined:
    22 Dec 2012
    Messages:
    188
    Thanks Received:
    4
    Location:
    Yorkshire
    Country:
    United Kingdom
    not sure tbh. they are screaming hot though all over the panels. I just think they are a bad design. horizontal rads shift a lot more air and have a far greater surface area with all the fins on a double panel.
     
  5. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    63,579
    Thanks Received:
    4,517
    Location:
    London
    Country:
    United Kingdom
    The heat output is expected to be in accordance with the maker's specification.

    You say they are hot all over.

    You also say you calculated the heat requirement. But are you sure you did that correctly?

    Why anyone wants to calculate in BTU is beyond me when kW have been the correct unit since 1980.

    As a very rough check, expect to need about 100W per square metre floor area.

    Tony
     
  6. needmorstuff

    needmorstuff

    Joined:
    22 Dec 2012
    Messages:
    188
    Thanks Received:
    4
    Location:
    Yorkshire
    Country:
    United Kingdom
    i did ok for every other room. lets say I miscalculated.. can you get fins to increase surface area?
     
  7. DP

    DP

    Joined:
    10 Dec 2003
    Messages:
    12,847
    Thanks Received:
    2,638
    Location:
    Glasgow
    Country:
    United Kingdom
    I for one can do heat loss in BTUs for a room without referring to charts and tables
    Secondly, lot of radiator specs still quote outputs in BTUs and Kw, so 1980 might be the cut off date but BTUs are still alive and quoted in 2017
     
  8. DP

    DP

    Joined:
    10 Dec 2003
    Messages:
    12,847
    Thanks Received:
    2,638
    Location:
    Glasgow
    Country:
    United Kingdom
    I do not think so
    How did you calculate the heat loss for the room?
     
  9. needmorstuff

    needmorstuff

    Joined:
    22 Dec 2012
    Messages:
    188
    Thanks Received:
    4
    Location:
    Yorkshire
    Country:
    United Kingdom
    I used a calculator on bestheating
     
  10. Sponsored Links
  11. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    63,579
    Thanks Received:
    4,517
    Location:
    London
    Country:
    United Kingdom
    To use the rough guide as a check on your calculations, what is your calculated heat loss in kW per square meter?

    And what is your total heat loss for the room?

    And the total radiator heat output?



    BTUs are sometimes quoted by manufacturers to help those dinosaurs who have not kept up to date with current methods.
     
  12. needmorstuff

    needmorstuff

    Joined:
    22 Dec 2012
    Messages:
    188
    Thanks Received:
    4
    Location:
    Yorkshire
    Country:
    United Kingdom
    I can always go from 1800 tall to 2100.. was just looking for a low cost easy fix.
     
  13. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    63,579
    Thanks Received:
    4,517
    Location:
    London
    Country:
    United Kingdom
    To use the rough guide as a check on your calculations, what is your calculated heat loss in kW per square meter?

    And what is your total heat loss for the room?

    And the total radiator heat output?



    BTUs are sometimes quoted by manufacturers to help those dinosaurs who have not kept up to date with current methods.
     
  14. transam

    transam

    Joined:
    20 Nov 2009
    Messages:
    24,060
    Thanks Received:
    3,102
    Location:
    Surrey
    Country:
    United Kingdom
    all rad out puts are quoted (?) by the manu at delta t 50 or 55 (?)

    years ago it was delta 60

    google it for an explanation . :)
     
  15. needmorstuff

    needmorstuff

    Joined:
    22 Dec 2012
    Messages:
    188
    Thanks Received:
    4
    Location:
    Yorkshire
    Country:
    United Kingdom
    horse has bolted fellas. calculations are meaningless now as the rads are already in. can't get fins so will need to either put up with it or drop some taller rads in.
     
  16. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    15,583
    Thanks Received:
    5,561
    Location:
    Lanarkshire
    Country:
    United Kingdom
    Last edited by a moderator: 11 Feb 2017
    • Like Like x 3
    • Thanks Thanks x 1
  17. Steelmasons

    Steelmasons

    Joined:
    10 Oct 2011
    Messages:
    16,405
    Thanks Received:
    3,969
    Country:
    United Kingdom
    In a nutshell.
     
    Last edited: 11 Feb 2017