Hi,
I'm planning on replacing my existing cooker with an Induction one and am looking for some advice regarding the associated electrical installation.
My existing cooker is connected through a 6 sq mm T&E cable and protected by a 32A mcb.
The proposed new cooker is a Rangemaster Excel 110 Induction model with a maximum load of 16.8kW at 230V. The manufacturer recommends connecting it through a 10 sq. mm cable and 45A mcb.
I intend having a new 10 sq. mm cable installed from the consumer unit to the Cooker Control Unit. The new cable will be approximately 15 metres long and it will be clipped under the floorboards.
The existing Consumer Unit is a Hager, but I cannot find a 45A Hager Type B mcb. I can only find 40 and 50A versions. I've had a look at an MK 45A Type B mcb, but the live input connection is not in the same location as the Hager mcb.
I understand that the 10sq. mm cable (in reference method C) should be able to carry about 64A, so from a cable protection point of view I should be able to use a 50A mcb. However, the Cooker Control Unit is rated at 45A, so is this likely to be an issue.
Any advise, or help, would be much appreciated.
Thanks
I'm planning on replacing my existing cooker with an Induction one and am looking for some advice regarding the associated electrical installation.
My existing cooker is connected through a 6 sq mm T&E cable and protected by a 32A mcb.
The proposed new cooker is a Rangemaster Excel 110 Induction model with a maximum load of 16.8kW at 230V. The manufacturer recommends connecting it through a 10 sq. mm cable and 45A mcb.
I intend having a new 10 sq. mm cable installed from the consumer unit to the Cooker Control Unit. The new cable will be approximately 15 metres long and it will be clipped under the floorboards.
The existing Consumer Unit is a Hager, but I cannot find a 45A Hager Type B mcb. I can only find 40 and 50A versions. I've had a look at an MK 45A Type B mcb, but the live input connection is not in the same location as the Hager mcb.
I understand that the 10sq. mm cable (in reference method C) should be able to carry about 64A, so from a cable protection point of view I should be able to use a 50A mcb. However, the Cooker Control Unit is rated at 45A, so is this likely to be an issue.
Any advise, or help, would be much appreciated.
Thanks