Yes.
Yes, and totally correct.
What about diversity?, that's 12kw or 50-52Amps in total!
That is true.6mm T&E supports 47 amps at a maximum, not accounting for voltage drop or de-rating factors.
Then you will be causing your customers unnecessary expense for unnecessary work.I would put the hob and oven on their own MCB if possible (Each wired in 4mm or 6mm with a 30A MCB/Fuse), if not you will need a 50Amp MCB/Fuse and 10mm cable.
As EFLI says, it will be fine. Especially with a BS3036 fuse in situ.
eveares - what is your position on applying diversity to a typical 110cm all-electric range cooker with an induction hob?
Why?I would have based it on around 75-80% of the total power.
You gave that impression.Ok, fair enough. Was not saying it would not be safe anyway,
Quite the opposite; it is your proposal which is not practical.just possibly not practical.
It's not a question of opinion.Never mind anyway, was only my opinion.
That's how it is done. It results in 22A (27A with socket)Are you also using the first 10A add 30% of remaining total current as the diversity?
That would require 10mm² cable with a 40A 3036.I would have based it on around 75-80% of the total power.
Have you ever come across such a circuit?
As you've been asked, why do you see a difference between an oven+hob (separate units) and a cooker (oven+hob in same unit)?All I was trying to say, is I initially and incorrectly assumed you would get no or very little diversity for a cooker/hob combo.
As above, what's all this obsession with 'separate'? You surely must have seen large cookers (with hob plus multiple ovens) 'all on one (probably 30/32A) circuit', haven't you? (one doesn't actually have a choice!)Yes..... but not in a domestic property, but I have also not ever seen a separate electric hob over 3Kw and a oven on the same circuit either.