chrishutt said:
...This amendment took effect from April 2002, so it appears that since that time vented hot water cylinders have been notifiable.
OK. Bottom line - my interpretation is still that vented cylinder installation or replacement is not notifiable.
The key wording is in the following amendment:
[code:1](4) After regulation 3(1) there shall be inserted the following paragraph -
" (1A) The provision or extension of a controlled service or fitting -
(a) in or in connection with an existing dwelling; and
(b) being a service or fitting in relation to which
paragraph L1, but not Part G, H or J,
of Schedule 1 imposes a requirement,
shall only be building work where that work consists of the provision of a window, rooflight, roof window, door (being a door which together with its frame has more than 50 per cent of its internal face area glazed), a space heating or hot water service boiler, or a hot water vessel.".[/code:1]
Whilst I agree that L1 added a requirement, my interpretation is that it was only in the context of "conservation of fuel and power", and doesn't add a requirement for the issue of a building notice.
In support of this interpretation, note the following amendment in SI 2001:3335.
[code:1]
Particulars and plans where a building notice is given
13.
(4) Where building work involves the provision of a hot water storage system in relation to which paragraph G3 of Schedule 1 (hot water storage) imposes a requirement, a building notice shall be accompanied by a statement which specifies -
(a) the name, make, model and type of hot water storage system to be installed;
(b) the name of the body, if any, which has approved or certified that the system is capable of performing in a way which satisfies the requirements of paragraph G3 of Schedule 1;
(c) the name of the body, if any, which has issued any current registered operative identity card to the installer or proposed installer of the system.[/code:1]
I've also had another look at the ODPM guidance document, and the wording in here concurs with my interpretation, namely:
[code:1](s) If I want to install or replace a hot water cylinder, will the
Building Regulations apply?
YES – if you are installing or replacing a hot water cylinder
within a vented hot water storage system (i.e. a system fed from
an open-ended pipe for venting).
The requirements are for the
installation to be energy efficient.[/code:1]
So, ODPM doesn't state that notification is a requirement, for a vented cylinder. In this regard it isn't wrong.
Finally, regarding Benchmark documentation, ODPM says:
[code:1]For either type of system your installer
should leave you with a completed
installation record and commissioning certificate. Some manufacturers attach
certificates to cylinders ready for installers to complete.[/code:1]
Note the use of the word "should".