You need to confirm the type of circuit it is, there are two main types of socket circuits.
* The ring final circuit, which will have a complete loop/ring of cables from the consumer unit through all sockets, then back to the consumer unit, this is generally run in 2.5mm2 T&E cable, on a 32A device at the consumer unit.
There will be two sets of cables (live (line), neutral, earth (CPC)), at each socket and two sets of cables at the consumer unit for this circuit, two in neutral busbar, two in earth busbar and two in the 32A MCB.
* The radial circuit, this would be one set of cable (live, neutral and earth), it is normally run in either 4.00mm2 T&E with a 32A MCB or 2.5mm2 T&E with a 20A MCB. The one set of cables will start at the consumer unit and again be routed between each socket outlet on the circuit, therefore you will have a neutral at the neutral busbar, earth at the earth buzbar and live at the 32A/20A MCB, but still have two cables at each socket outlet, until you come to the very last socket on the circuit where there will be only one set of cables, as this circuit does not return back to the consumer unit.
A few things to look at for when determining what type of circuit you have is:
Existing spurs, these can be feed via a socket outlet on the circuit, a fused connection unit or they could be hidden or accessible within the fabric of the building via junctions and jointing methods.
So to determine the circuit you have would require some investigation and some testing of the conductors, to confirm what you have.
The reason you need to confirm the type of circuit you have and if there are any existing spurs on the circuit, is that the ring final and the radial circuit are designed, installed and load shared differently.
So this would then determine how you would either extend or spur from.
//www.diynot.com/wiki/Electrics:Socket-Circuits
https://www.tlc-direct.co.uk/Book/6.3.3.htm
https://www.tlc-direct.co.uk/Book/6.3.2.htm