Previous owners had a big range cooker on 6mm sq cable from CU 40 amp MCB via cooker connection unit. I only have a donated 2.6KW oven as can't afford what they took out. As this works out as drawing 11.3amp would I be best to just plug it in through a 13amp plug or can I replace the MCB for a lower rated one so to keep it on its own radial? I'd prefer it to be on the seperate MCB as I can then utilise the switch on the CCU to isolate it quickly.