Hi..I have 3 20w outside led spots connected to 6A RCD..there is a fault somewhere which i haven't looked for but the 6A doesn't trip, its the 63A that trips..any ideas


63A?
Sounds like a single RCD, protecting several circuits, or perhaps the entire CU.
Sounds like a single RCD, protecting several circuits, or perhaps the entire CU.




Hi..I have 3 20w outside led spots connected to 6A RCD..there is a fault somewhere which i haven't looked for but the 6A doesn't trip, its the 63A that trips..any ideas

tests the RCD but it is unlikely to be faulty, the clamp on
can test when live, and the insulation tester
when dead both testers cost around £35 each but they also need some skill to use them. So the start point is look for water ingress. This is most likely cause, the problem is the insulation tester used 500 volt DC and the house uses AC and the clamp on will only work when it has not tripped.It should but will it?This should help identify what trips,