Lincat griddle 3kw

Discussion in 'Electrics UK' started by OvertonPlumber, 27 Oct 2019.

  1. OvertonPlumber

    OvertonPlumber

    Joined:
    25 Jan 2007
    Messages:
    1,956
    Thanks Received:
    376
    Location:
    London
    Country:
    United Kingdom
    Hi all ive aqquired a 3kw commercial 600mm Lincat griddle. Unfortunately we cleaned it up before fully testing it.
    It runs of a 13amp plug.
    At first i had it plugged into my shed circuit which is on a 16 amp radial fed from my garage. It would trip the Rcbo after about 2 minutes, this would not reset without unplugging the griddle.
    We then moved it to the garage and put it on the 20amp rcbo ring. After about 3 minutes it tripped that Rcbo.
    What i did notice when i was cleaning the unit was the earth spade was disconnected on the power connector inside the unit, i duly reconnected it, however as the Rcbo trips on leakage to earth would having it disconnected allow it to work?.
    The garage CU runs 100 amp fed from the incoming house supply. Was put in to run my 200 Amp inverter Tig welder.
    Gonna get my sparks to do a insulation test on the element and probably change it.
     
  2. Sponsored Links
  3. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,901
    Thanks Received:
    1,980
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    It might work, but when the element fails, the whole casing of the appliance would become live and sit there waiting to kill someone who was unfortunate enough to touch it.
     
  4. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,527
    Thanks Received:
    2,132
    Location:
    Oxfordshire
    Country:
    United Kingdom
    It’s possible that after a hundred cycles of switch on and trip, the element will have dried out. Or maybe there is a more fundamental problem.
    But, whatever the issue is, for your own safety, as Flameport said, reconnect that earth connection. It’s there for a reason.
     
  5. OvertonPlumber

    OvertonPlumber

    Joined:
    25 Jan 2007
    Messages:
    1,956
    Thanks Received:
    376
    Location:
    London
    Country:
    United Kingdom
    Well that was my first reaction that i reconnected it. However it dawns on me that someone before me disconnected it to get round nuisance tripping.
     
  6. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,504
    Thanks Received:
    415
    Location:
    Kent
    Country:
    United Kingdom
    Yes very possibly.
    What that really means is the plate is likely to be live, that's the most likely reason it trips...
     
  7. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    37,119
    Thanks Received:
    1,288
    Country:
    United Kingdom
    After 2 or 3 minutes?
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  9. Sponsored Links
Loading...

Share This Page