Its your equipment, so it is upto you to get an electrician to replace it, though two points
1) what sort of load do you have downstream of it? (big electric shower, cooker? lots of appliances... wylex 60A standard range boards on 100A fuses don't actually tend to cause problems because generally things arn't running at the limit limit, if it was popping a 60A fuse every week before it was upgraded to 100A that would be a problem for example. Its not really a good situation, but it doesn't mean its going to explode tommorow, it would be a pir code 2 IMHO unless it looked to be heavily loaded
2) Are you actually sure its a 100a fuse, just because the carrier says 100A on, doesn't perclude the possibility that the fuse link inside is smaller (there is no easy way to find out, just bear in mind, that it might not neccesalily be 100A)