mains smoke alarms

Joined
23 Mar 2005
Messages
265
Reaction score
4
Country
United Kingdom
i have interconnected 3 mains smoke alarms using 3 core and earth.
i was intending to run them off the lighting circuit.
but i`ve now decided to go back to consumer unit and 6amp fuse.
what cable do i use to go from mains to first alarm?
cheers
mark
 
Sponsored Links
If you thought 3 core, what were you going to connect the third core to at the CU?
 
yeah i meant what size twin and earth?
1.5 or 2.5?
 
Sponsored Links
1.0 or 1.5 TE

At 6 amp you can use either, even 2.5 if that's all you have.

Do pay attention to the smoke detector warnings, they don't like ins res test and go pop if you do test them with the units in situ.
 
thanks for that.
i can run the cable in now.

"they don't like ins res test and go pop if you do test them with the units in situ."
can you explain this though please
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top