I'm a bit late in this conversation, but...
But how about a combined mains smoke and CO detector, one that has two different sounds for each type of alarm?
I like your thinking...
3A or 6A MCB regardless, both 1mm² and 1.5mm² are usually suitable in most domestic situations.
I think on that one we can agree that "sheathed or unsheathed cable" is talking about non flexible cables. Either way I agree that it is very silly and utter nonsense that you can use 1.0mm² Flex but not 1.0mm twin and earth!
Also what happens if you had a lighting circuit with smoke alarms wired in 1.0mm² T&E and then you later removed all the lights from the circuit. Also has anyone considered the possibility of that if you add smoke alarms to a lighting circuit, that it may technically become a "power circuit" and thus 1.5mm² is required if you use T&E?
Also, CO detectors if interlinked with smoke detection will require an alarm controller to indicate cause of alarm (smoke/CO).
But how about a combined mains smoke and CO detector, one that has two different sounds for each type of alarm?
52.3 is nonsense. It is not possible to comply with regulations which are nonsense. 52.3 has to be ignored.
I like your thinking...
Well 3A mcbs are not a common device
3A or 6A MCB regardless, both 1mm² and 1.5mm² are usually suitable in most domestic situations.
You could, of course, use flexible cable in which case it is allowed to use a smaller csa unless you consider 'sheathed or unsheathed flexible cable' is also a 'sheathed or unsheathed cable' in which case you can't.
I think on that one we can agree that "sheathed or unsheathed cable" is talking about non flexible cables. Either way I agree that it is very silly and utter nonsense that you can use 1.0mm² Flex but not 1.0mm twin and earth!
Also what happens if you had a lighting circuit with smoke alarms wired in 1.0mm² T&E and then you later removed all the lights from the circuit. Also has anyone considered the possibility of that if you add smoke alarms to a lighting circuit, that it may technically become a "power circuit" and thus 1.5mm² is required if you use T&E?