Interestingly, there is a section in the ECA's guide to the 17th entitled "the futility of testing Zs on an RCD protected circuit" or something very similar.
They say that RCD protected circuits do not have to meet the Zs requirements as the RCD guarantees that the required disconnection time is met. All that is needed is to test the RCD.
That's ridiculous. Here's why:
1. The regs demand circuits to be designed correctly: The breaker type would have to suit the EFLI, regardless of whether the circuit was RCD protected or not.
2. A 30mA RCD is only good up to 1666 Ohms. What if you tested the RCD which was fine but you did not test the Zs, which just happened to be >1666 Ohms?
Then the RCD would not be guaranteed to give the required protection.
Its not ridiculous, quite the opposite. Its correct. Heres why:
1. The regs state if the circuit is protected by an RCD the maximum Zs is determined by InR < 50V. There is no regulation that states "the breaker type must suit EFLI conditions" - nonsense. The breaker is selected in accordance with the designed load, breaking capacity vs PFC etc.
2. Nobody is saying dont test Zs to make sure that (for a 30mA device) that Zs < 1666 Ohm. If it "just happenned to be greater" then it would fail BS7671 and you wouldn't energise the circuit !